NH3LVR
12-12-2017, 10:57 PM
I received a call from my old employer today.
Years ago I replaced a oil heater in a screw compressor near here. The unit has two heaters installed in 3 or 4 inch block welded into the oil sump.
According to the operator that heater is still operating fine.
However the replacements seem to be overheating and burning out fairly quickly. I have not looked at the machine, but I am told that the replacements have a side clearance of about 1/8 of a inch when installed. (Being retired I will not be seeing the machine)
I do not remember using any heat transfer compound when I installed the heater, nor do I remember if there was excessive clearance. We would have bought the heater from the OEM.
My usual procedure was to use something like a Nickel based Anti-Seize compound.
Removing the functioning heater is not a good plan as it may well break if they try to remove it for identification.
The OEM (McCormack) is no longer in business.
Can someone suggest a heat transfer compound that can be installed in a vertical application?
I actually worked for the OEM at one time, but I do not recall what we used.
I have asked for an Amp reading from the functioning one so we can determine the electrical sizing.

Grizzly
13-12-2017, 12:13 AM
Really nice to hear from you "Old Timer"!
If I could I would help.
But Sadly the kit you need help with is something I have not come across on this side of the pond.
Out of interest are the Heaters wired in parallel or series?
Cheers Grizzly

NH3LVR
13-12-2017, 01:01 AM
Same to you Grizzly.
Do not have much to post about these days. Sure nice to do other things than get up and go to work. I do not know how I ever had time to have a job.
The heaters fortunately are in parallel.
Only one heater working is a problem as although they are inside the area is cold.

RANGER1
13-12-2017, 06:57 AM
NH3LVR,
Not 100% sure but older type immersion heaters we used were filled with fridge oil & had a breather hole so to allow for expansion etc.
These pockets were on 30 deg angle & breather at top part of pocket.
Heater had a t/stay up the middle like Vilter.
Some other heaters, no pocket, but direct contact.
If it is sealed & filled with oil or heat transfer paste there is a possibility for hydraulicing pocket if no vent.