Hi Guys,
Have a prob with a U4 fault on this single unit, have 30vdc coming of outdoor unit comms to earth wire 2vdc of indoor unit.
Checked drain -all clear, powered down and up no joy.
Flaps opens and closes on indoor -power 230v ok
suspect indoor unit pcb, any advice would be welcome

frank
02-03-2016, 07:51 PM
I would run a temporary single core wire between terminal 3 of the indoor and outdoor units to see if that solved the problem

nike123
02-03-2016, 08:03 PM
Check that terminal 1 and 2 on indoor and outdoor are correctly wired ( not mixed)!

subcoolfm
13-03-2016, 05:47 PM
I may be your saviour.

Is the led lit on the outdoor pcb?

if not, unplug outdoor fan motor, is it now lit (blinking)

try the outdoor eev head too,