PDA

View Full Version : McQuay Chiller Problem



chetan7788
27-01-2015, 05:09 PM
HI,

I have a mcquay chiller PFS 330.3 ( china ) with Siemens controller.
It does not show any alarm but still the compressors are not taking the start command.
the startup time is set at 180 sec and the countdown is not starting.Kindly help

GREEK_REF
29-01-2015, 07:25 PM
Hi first of all check the evaporators water flow, clean strainer, make sure pump works properly or the flow switch!! If you don't have enough Δp the machine will not start.

AlexG
31-01-2015, 04:41 PM
Did you check remote on-off contact?

chetan7788
13-03-2015, 03:23 PM
Thanks guys.It was the flow switch issue.

chetan7788
13-03-2015, 03:26 PM
Hi,

I have a McQuay PFS 330.3 . Date is not getting updated in the chiller controller.
I am using the admin login but still no success. Please suggest.