Log in

View Full Version : Spectrum SB 30 full of ***** but running in a vacuum



shix
07-01-2015, 07:05 PM
I am working on a spectrum that has the rear unit disconnected. The unit has a newly rebuilt throttling valve on it and I just charged it. The unit is full of ***** but it is running in a vacuum. The high side pressure is stable around 135psi and the low side is in a vacuum. It is cooling but only at a -7* differential.

Brian_UK
07-01-2015, 07:19 PM
Is the rebuilt valve working?

cadwaladr
07-01-2015, 09:25 PM
Drier,txv?

gravy258
08-01-2015, 05:48 AM
check the LLS diode is energised on the relay board(liquid line solenoid) Bottom left corner of board.
If it is, probably TX valve or power head fault

pcvh1976
09-01-2015, 09:08 AM
your problem most be found in the liquid line, check also if your LP-gauge is correct.

mbc
09-01-2015, 11:01 AM
all suggestion might be right,

what is a your refrigeration gas ? why your hp pressure is a 135 psi

if your using R-22 it should not be less than 180 psi , Min. TX valve works pressure to works and open correctly

gravy258
10-01-2015, 01:05 AM
all suggestion might be right,

what is a your refrigeration gas ? why your hp pressure is a 135 psi

if your using R-22 it should not be less than 180 psi , Min. TX valve works pressure to works and open correctly

it'd be R404a , the OP should of posted in the TRANSPORT section.