PDA

View Full Version : Pego 200 expert connections of safety .....



Palkoper
12-07-2014, 09:13 PM
Hi there its my first touch witch install of freezer with controller pego 200 expert and I am not sure where to connect ranco high and low pressure switch for safety of compressor .... Please any advice thanks.

install monkey
12-07-2014, 09:30 PM
if theres a contactor or relay for the compressor then switch the live feed to (A1) throught the pressure switch - ranco pressure switches are rated for 16 amp

joe-ice
13-07-2014, 01:51 PM
Or connect the pressure switches through common and inp1 compressor protection input .Set parameter In1 to 0 and parameter pc to 1 which is normally closed