View Full Version : 248 volt, open winding
Royal241
20-05-2014, 12:10 AM
I have a 200v-230v 1 phase compressor that has the common winding open. Took power off, got back to it in 4 hours, same result, protector doesn't close. Checked voltage: 248 volts. Can this be the cause of the burn out?
Rob White
20-05-2014, 12:44 AM
.
That is about 8 - 9% over??
I know of sites that are rated 230v and we get 252v which is near to the 10% maximum.
It is possible, but probably unlikely.
Rob
.
Royal241
20-05-2014, 12:59 AM
[QUOTE=Rob White;295950].
That is about 8 - 9% over??
I know of sites that are rated 230v and we get 252v which is near to the 10% maximum.
It is possible, but probably unlikely.
Rob
I will replace it tomorrow and will cut open the old one to see what happened.