05-02-2014, 01:56 PM
Hello,
I'm doing commisioining duct-split unit (DX system),
detailed outdoor-unit with a scroll compressor copeland ZR72KC-TFD (I max 12A)
R407C charge, indoor-unit with cooling coil capacity 14.3kw with danfoss expansion
TGEX-6TR-20kw (P.N.067N2236)
T room control setting at 24C.
after vacuumizing and charging R407C, start-up and running the unit,
after 12 hours running,
T room is still too high at 25-27C
Suction pressure = 80PSiG and liquid pressure = 270 PSiG
the compressor I run = 8 Ampere
what's about wrong with this unit??
I'm confused why the suction pressure can be high (80 psig)
My last bit of waste refrigerant (from liquid line), and then
pressure turns into P suct = 80PsiG P liquid = 255 psig
Please opinion or input to have experienced the above case.
I'm doing commisioining duct-split unit (DX system),
detailed outdoor-unit with a scroll compressor copeland ZR72KC-TFD (I max 12A)
R407C charge, indoor-unit with cooling coil capacity 14.3kw with danfoss expansion
TGEX-6TR-20kw (P.N.067N2236)
T room control setting at 24C.
after vacuumizing and charging R407C, start-up and running the unit,
after 12 hours running,
T room is still too high at 25-27C
Suction pressure = 80PSiG and liquid pressure = 270 PSiG
the compressor I run = 8 Ampere
what's about wrong with this unit??
I'm confused why the suction pressure can be high (80 psig)
My last bit of waste refrigerant (from liquid line), and then
pressure turns into P suct = 80PsiG P liquid = 255 psig
Please opinion or input to have experienced the above case.