View Full Version : Climaveneta Chiller problem
anil130
21-11-2013, 03:07 PM
Hi frens...
we had installed two Climaveneta chillers on the Hospital, Model number: NECS-N/D/B 2818 and the S/NO:32023515
the problems found on the chillers are as follows:-
Chiller No. 1
Compressor of circuit trips with in a minute and shows Compressor fault error..
CHILLER NO- 2
Compressor of circuit trips with in a minute and shows Compressor fault error.
what will be the main reason behind it and waiting for the prompt reply..!!
Cheers...
marc5180
21-11-2013, 06:05 PM
Hi frens...
we had installed two Climaveneta chillers on the Hospital, Model number: NECS-N/D/B 2818 and the S/NO:32023515
the problems found on the chillers are as follows:-
Chiller No. 1
Compressor of circuit trips with in a minute and shows Compressor fault error..
CHILLER NO- 2
Compressor of circuit trips with in a minute and shows Compressor fault error.
what will be the main reason behind it and waiting for the prompt reply..!!
Cheers...
Hi, it could well be the compressor has overheated or the motor protector module is faulty (if that model has one)
install monkey
21-11-2013, 06:16 PM
does it have phase protection??- swap phases over in case compressors running backwards
bigor_2
21-11-2013, 07:24 PM
check the presence of three phases before\after on compressors contactor.
anil130
22-11-2013, 01:55 AM
ok frens..
today i will check and revert back to you....and any body have service manual of this model number..it will be highly appreciated..
anil130
23-11-2013, 01:15 PM
Dear frens..still the chiller had same problem
Chiller No. 1
Compressor of circuit no 4 trips with in a minute and shows Compressor fault error.
We are running this chiller by isolating the fault circuit.
CHILLER NO- 2
Compressor of circuit no 3 and 4 trips with in a minute and shows Compressor fault error.
We are running this chiller by isolating the fault circuit.
only 8 compressor were working now..if some body have service manual of this chiller then i will be
highly obliged.
nike123
23-11-2013, 04:46 PM
Power source quality could be a issue!
Check voltages, voltage drop and balance of phases!
bigor_2
24-11-2013, 01:07 PM
new units. first start. compressor blocked. it is very strange! do you check power supply?
Murre
08-12-2013, 02:07 PM
What about the refrigeration charge? Is it charged by factory with HFC or nitrogen?
anil130
09-12-2013, 02:15 PM
@Murre: It was charged by Factory HFC...i found expansion valve is not working..
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.