MarcoL
08-08-2013, 08:55 PM
Hi. I've a big problem with some noisy (chattering) check valves.
The refrigerating circuit of the chiller has:
- 3 Frascold semi-hermetic compressors (R407C, 60HP)
- antivibrating/flexible piping
- NRV Danfoss check valve (42mm)
So there are 3 compressors in parallel operation in the same circuit.
Last week we tested some different valves (Italian Brand), with Kv=35 and they were noisy.
Now we installed NRV check valve (Kv=29) but they are still very noisy.
When the 1st compressor starts up, there are no problems.
Then 2 or 3 compressors are working simultaneously, all the valves are noisy.
The diameters of the lines are: 42mm for each compressor and then the discharge pipe/collector is 64mm.
Possible solutions:
- we are trying to install a bigger discharge pipe, 88.9mm, to reduce the speed inside the discharge pipe, after the check valves
- another idea is to use NRVH valves instead of NRV, with strong spring (please, consider that we've already installed NRV valves after semi-hermetic compressors in a huge number of chillers, without problems)
- someone suggest me to install the check valve near the compressor, before the flexible pipes
What do you think about the problem ? Do you have any advice ? Thanks
The refrigerating circuit of the chiller has:
- 3 Frascold semi-hermetic compressors (R407C, 60HP)
- antivibrating/flexible piping
- NRV Danfoss check valve (42mm)
So there are 3 compressors in parallel operation in the same circuit.
Last week we tested some different valves (Italian Brand), with Kv=35 and they were noisy.
Now we installed NRV check valve (Kv=29) but they are still very noisy.
When the 1st compressor starts up, there are no problems.
Then 2 or 3 compressors are working simultaneously, all the valves are noisy.
The diameters of the lines are: 42mm for each compressor and then the discharge pipe/collector is 64mm.
Possible solutions:
- we are trying to install a bigger discharge pipe, 88.9mm, to reduce the speed inside the discharge pipe, after the check valves
- another idea is to use NRVH valves instead of NRV, with strong spring (please, consider that we've already installed NRV valves after semi-hermetic compressors in a huge number of chillers, without problems)
- someone suggest me to install the check valve near the compressor, before the flexible pipes
What do you think about the problem ? Do you have any advice ? Thanks