Log in

View Full Version : the compressor's cooling capacity difference from Bitzer selction software



Jiazi
02-08-2013, 07:02 AM
Hi,all
The bitzer software, under 2-stage semi-herm. reciprating compressor, they have two cooling capacity data, Qo & Qo*, and they are different.

What's the differnce between them? The Bitzer's paper catolog always list Q0*, so what's the fuction of Qo?

Thanks

10604

The Viking
02-08-2013, 10:10 AM
Different standards of calculation by the look of things, the Qo* is calculated to EN 2900 standards.

:cool:

Jiazi
02-08-2013, 12:46 PM
Then what the standard for the Qo? what's Qo used for?

Regards
Jiazi

Peter_1
03-08-2013, 06:12 AM
The first is with the inputs you gave in and the second wit asterisk is calculated using the EN2900 standard, mostly other SH and SC than you specified in your inputs; EN2900 uses standard values.

Jiazi
04-08-2013, 02:28 PM
Thank you all for your kindly input

D.D.KORANNE
20-09-2013, 11:14 AM
While selecting compressor maintainthe diffrence between evaporating & suction gas temp at about 20.