PDA

View Full Version : hitachi install



rbartlett
16-02-2006, 08:15 PM
hi guy's

we are about to do a 7kw 410a HP anyone know the precharged pipelength??

cheers

richard

eggs
16-02-2006, 10:46 PM
if it's a G8 cassette they are usually 30m.

cheers

eggs

jan
20-02-2006, 09:33 PM
hi guy's

we are about to do a 7kw 410a HP anyone know the precharged pipelength??

cheers

richard
A dutch market 7kw hitachi unit(ras-3HRNV) is developed for 10 meter but there is enough 410a for a max of 30 meter.the max piping length is 60m.
if you want to do it exactly you must fil til 30-40mtr 0,6 kg 410a/ til 40-50mtr 1,2kg and til 50-60mtr 1,8 kg 410a.

Danno
23-02-2006, 03:05 PM
Hi, These units are charged for 30m then add 60g/m upto 60m

Regards

afeef
26-02-2006, 07:22 AM
hi
it depends apon the distance between the outside unit and the inside unit,,,but no less than 5 meters
ok
afeef