View Full Version : lennox r410a heat pump



GHAZ
14-07-2013, 12:24 PM
hi friends i have a problem with this chiller. This week its been very hot about 30c ambient temperature.got a call out to see why wasnt working.got site and found c1 fans not comming on and c2 empty of gas.the fan inverter wasnt sending any power to fans its a altiver 21.so by pass it and ran fans direct and it ran for 2.5 hours good. Brought temp from 36c to 14.8c and then the pressure unit its armstrong went out on fault and shut the chiller down on bms.refilled the pressure unit got pressure upto.0.9b and restart the chiller. It ran for 20 minutes and it went off again on pressure unit.found the bladder empty of pressure so pumped air into the bladder and fill it up with water again. But still shows fault on bms and chiller wont run. The chiller has it own electronic flow switch and customer has sontay pressure switches. The water flow is 2bar in and 1.5 bar out of evaporater.the chiller shows on service display is unit on. Enabled c1. Comps waiting flo. Switch on. Hp off lp on. Im stuck on what to do next.how to get it going or how to by pass bms. any help will be great ful

install monkey
14-07-2013, 01:13 PM
http://www.mediafire.com/download/hi2k9w1bwquvilk/PCO-CS-UM-GB-1_14_LENNOX.pdf
has the expansion vessel bellows held at 1 bar or has it leaked back into system?

GHAZ
14-07-2013, 01:38 PM
Hi the xpansion vessels bellows pump upto 8 psi and unit water pressure upto 1.2 bar. But im going back tomorrow and try again. Is there any way to by pass these things to run the chiller for few seconds just to prove the chiller is ok

install monkey
14-07-2013, 01:44 PM
bms can be bypassed - usually its just a remote on/off signal and a common fault signal. check external wiring going into the chiller.
check control panel for bms for chiller relay- maybe manually latch it to enable output

pressurisation unit will only alarm on hi/low pressure and constant fill-leak prevention- as long as ur system is between 1-3 bar shouldnt be an issue

GHAZ
14-07-2013, 02:04 PM
Thankyou friend

install monkey
14-07-2013, 03:02 PM
does the chiller have a dc50 controller- because you would need a ds50 service tool to reset a major alarm- and also easier for reading alarm history and thermister values

GHAZ
14-07-2013, 06:00 PM
Yes it does have a ds 50 service controller and ive reset all alarms on it and when you check rhe comps it say comps wait.flow,state on

install monkey
14-07-2013, 08:42 PM
state on - signal for comp run- unless external safety devices holding it off- pressure switch/flow switch

GHAZ
14-07-2013, 09:55 PM
Im there tomorrow morning again and ill give an update to what has happen

GHAZ
17-07-2013, 06:55 PM
Hi install its the carel pco board that isnt sending signal. Got lennox comming out to replace soon.thankyou for your help friend

Peter_1
17-07-2013, 06:56 PM
Ghaz, your avatar is an opened Bitzer. Why you opened it? We have a similar machine with exploded oil filters in the compact screw.

Peter_1
17-07-2013, 06:56 PM
An it's also in a Lennox but on R407c

GHAZ
17-07-2013, 11:29 PM
Hi peter my picture is of an csh 85 bitzer i open it to change the oil seperater o ring and internal oil filter because the previously motor burnt on it

Peter_1
18-07-2013, 08:02 AM
Was the machine old and ran it a lot of hours? Did your rewind the motor?
We have on a Lennox now in 4 years 5 burnt compressors

GHAZ
18-07-2013, 05:33 PM
Yes machine wasnt that old it was on r407c gas wirh water pumps built on chiller and 2 times pump fail and then on circuit 2 two compressors burn out and finaly the evaporater had burst it copper tubes and the chiller got scrapped