View Full Version : budget cost for henry dual PRV valve
r.bartlett
08-06-2013, 12:01 AM
chaps I am waiting for prices back from suppliers but they are very slow and client is chasing me to get my price in by monday. Can anyone give me a realistic price for a henry dual PRV
http://www.henrytech.co.uk/wp-content/uploads/2012/10/77_Sentry-Safety-Device-Assemblies.pdf
ball park figure chiller with 2 x with 30kg R407c circuits
Quality
08-06-2013, 12:08 PM
Its about £80 - £120 per valve
For recalibration
Richard
Is it the assembly or the valves you need?
alec
r.bartlett
08-06-2013, 10:22 PM
we are swapping a single for a dual assembly so will need the full kit -one per circult.I am guessing about £500 ea??
You would be well covered at that, wholesalers are slow to price because it's a rare service replacement part, normally factory fitted. I have an assembly if you get caught out.
alec
r.bartlett
08-06-2013, 11:12 PM
You would be well covered at that, wholesalers are slow to price because it's a rare service replacement part, normally factory fitted. I have an assembly if you get caught out.
alec
Thanks
just quoting out atm so just need to price them as I was chased hard on Friday for the quote:-)
james10
09-06-2013, 12:21 AM
Around £80 per 1/2" PRV and similar for the valve, fit them all the time, you should ask your clients if they require certificated valves as there is an additional charge and longer lead times for the test certs
r.bartlett
09-06-2013, 09:48 AM
Around £80 per 1/2" PRV and similar for the valve, fit them all the time, you should ask your clients if they require certificated valves as there is an additional charge and longer lead times for the test certs
Has to be the complete dual assemblies
All PRV's supplied here have certs as standard, i thought it was a requirement?
alec
james10
09-06-2013, 08:35 PM
Has to be the complete dual assemblies
You build them yourself buy 1x dual shut off valve and 2x prvs and assemble
Grizzly
09-06-2013, 10:01 PM
Hi Richard.
HRP come out much cheaper with their on-line listed prices.
However you may get much better discounts at Climate Center.
HRP =
PRV with cert approx £67.00
Rupture disc Assy Approx. £80 ish
Dual Manifold £72.00
Say just over 200 ish.
CC =
PRV mid 50's to 60's ( not sure if they are with a cert?)
Rupture disk £110.0
Dual Shutoff £105,00
Yuo Choose.
Grizzly.
r.bartlett
09-06-2013, 10:27 PM
Hi Richard.
HRP come out much cheaper with their on-line listed prices.
However you may get much better discounts at Climate Center.
HRP =
PRV with cert approx £67.00
Rupture disc Assy Approx. £80 ish
Dual Manifold £72.00
Say just over 200 ish.
CC =
PRV mid 50's to 60's ( not sure if they are with a cert?)
Rupture disk £110.0
Dual Shutoff £105,00
Yuo Choose.
Grizzly.
Cool that's as close as I need it.. :-)
Grizzly
10-06-2013, 06:55 AM
All PRV's supplied here have certs as standard, i thought it was a requirement?
alec
They usually are here Al.
There are very few instances where they would be changed.
Other than when they are out of date as defined by the Insurance assessor and their written scheme.
Which commonly is every 5 yrs although it can be required more frequently.
Not all chillers have to have their PRV's changed, but that is another story!
Grizzly
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.