30-05-2013, 02:15 PM
Dear Friends:I am facing problem of low temperature attain in ice cream freezers(-26C), the top five coils of evaporator do cooling while the below 8 did not as the throw is also at the top. Freezer is charged with R 404a with Danfoss compressor, capillary tube and 1/6 condenser, fan cooled.Any idea how can I troubleshoot the problem.regards:

ATR
01-06-2013, 04:34 AM
You talking about a 1/6 HP compressor right? This is a little reach in type unit? Is it a chest or stand up? What exactly do you have here?

1mikeefc1
02-06-2013, 08:43 AM
It sounds short of gas but without any more info its shooting in the dark mate.

drewynp
03-06-2013, 02:08 PM
What's your superheat? Cap tube system not getting enough refrigerant to satisfy the evap? Sounds pretty cut and dry to me.

kamrannasir
04-06-2013, 11:50 AM
Yes, that is a chest freezer...

kamrannasir
04-06-2013, 11:51 AM
What is the best method to identify the quantity of refrigerant, I mean, is that sufficient or not?

1mikeefc1
04-06-2013, 08:42 PM
Putting your gauges on the compressor and checking gas charge is correct would be the best method.

The MG Pony
21-06-2013, 02:34 PM
? Sounds low on charge, first step is to find where did the rest of the charge go! If it is really old then just slow bleed and probably safe to suck it down and recharge via the labled weight, if there is no lable any more, add say 2 or 3 ounces and let it run, watch the return gas temp (Sensible) till it is cool (add bit of gas if needed till it is cool for the compressors sake!), let it run down to operating temp, or as close as you can get it, then slowely add refrigerent till you get the super heat to about 20k let it keep running to it's lowest Tstat seting once it is opperating at it's design temp check and adjust SH no lower then 15K.