View Full Version : daikin decos 3f allarm in pty j241
giacar
22-05-2013, 10:46 PM
hello to all
I have a problem with a machine Daikin
alarm j241
model building in January 2013 lxe10e133 sensation valve dsv
the valve DSV nn is installed to factory.
controller decosIIIf
Can you help me??
waterskidog
25-05-2013, 06:22 AM
manual says,
DSV does not
open
Does this alarm every time or does the alarm go away? I would try another coil and check connection all the way to the controller.
Copy and paste address below to download manual.
http://l.bitcasa.com/CkmManwg
giacar
25-05-2013, 09:14 AM
only in pty.
nn is the dsv.
I include photos.10412104131041410415
install monkey
25-05-2013, 06:41 PM
coil has been replaced- ensure voltage when in defrost mode, use a coil lifter to see if the body actually allows flow