Log in

View Full Version : bitzer screw compressor fault



yair be
30-04-2013, 04:41 PM
Dear friends
Why is the suction pressure rises with bitzer screw compressor starting.
This is a freez compressors rack for supermarket application.
When closing the tap down the compressor suction goes to vaccum.
thanks
yair

Coorsman777
30-04-2013, 06:40 PM
Right rotation?

yair be
01-05-2013, 05:05 PM
Right rotation?

yes the rotation right.
also i can say that the compressor has been worked in right condition for a 500 hr with out eny fult. and the oil prssure was right to.

RusBuka
01-05-2013, 07:26 PM
May be he doesnt loading?

NoNickName
02-05-2013, 09:29 AM
Internal safety valve leaking from high to low side.

yair be
02-05-2013, 09:58 AM
dear friend
the safty valve is new we replace it .
we steel have the problem.
thaks,
yair

yair be
02-05-2013, 10:11 AM
dear friend ,
I checked and it looks normal unloading.
anyway on Starting there is a trend of moving high pressure towards the suction pressure .
thanks,
yair

NoNickName
02-05-2013, 11:00 AM
You've still got a bypass somewhere. Sometimes is installed on purpose to reduce the inrush current.