wufei_adi
26-04-2013, 03:13 AM
Hi,
Greetings and I am new here, previously I work as Industrial Automation and Electrical Engineer but now im moving into HVAC field. This is completely new for me.
I am now working in a project of HVAC, Here some of the calculation i've done ;
OAHU-1
154800 Kcal/H
10500 CMH
516 L/min
AHU-1
16340 Kcal/H
14500 CMH
54.5 L/min
AHU-2
26660 Kcal/H
13300 CMH
89 L/min
I have found the formula to convert Kcal/H to kW
for example AHU-1
16340 / 5 = 3668
then
3668 / 60 = 54.5 kW (but this is not Electrical Motor Power Consumption)
How to calculate the estimation of Electrical motor Power Consumption (kW) ?
Thank you
Greetings and I am new here, previously I work as Industrial Automation and Electrical Engineer but now im moving into HVAC field. This is completely new for me.
I am now working in a project of HVAC, Here some of the calculation i've done ;
OAHU-1
154800 Kcal/H
10500 CMH
516 L/min
AHU-1
16340 Kcal/H
14500 CMH
54.5 L/min
AHU-2
26660 Kcal/H
13300 CMH
89 L/min
I have found the formula to convert Kcal/H to kW
for example AHU-1
16340 / 5 = 3668
then
3668 / 60 = 54.5 kW (but this is not Electrical Motor Power Consumption)
How to calculate the estimation of Electrical motor Power Consumption (kW) ?
Thank you