View Full Version : McQuay inverter hp chiller



waseem naamo
14-04-2013, 12:26 PM
Dear All

I have a problem with chiller made by McQuay
Air cooled - inverter - heat pump

the problem : chiller did not stop at outlet water temp setpoint ( 7 C ) , it is still working down to antifreeze setpoint ( 3 C )

Please advise asap

Brian_UK
14-04-2013, 08:05 PM
Recalibrate thermostat to switch at correct point.

goshen
18-04-2013, 11:48 AM
Hi
check what sensor is set to regulate your water temp.
ewt or lwt , the sensor could be out of cal as brian said or your settings are wrong.
good luck

waseem naamo
21-04-2013, 07:02 PM
water sensors are calibrated , i set it as water leaving temp
the problem that 3 units have same fault ????

install monkey
21-04-2013, 07:19 PM
http://www.refrigeration-engineer.com/forums/showthread.php?38857-Chiller-fault