Hi, when i am strength testing a 410 system ,how long do i leave it at that pressure?
Regards brian

martinw58
04-04-2013, 09:14 PM
there is no set time for strength test I test for up to 30 mins then leak test for 24 hrs

nosidam
04-04-2013, 09:41 PM
cheers martin, I have been strength testing for about an hour,so not to much difference. can a leak test and strength test be done at the same time for example, if you have a system with no joints and you test with leak spray whilst doing a strenght test?

martinw58
06-04-2013, 07:26 AM
thay need to be seperate as ofn has larger molicules than 410a so takes longer to leak

nosidam
06-04-2013, 07:50 AM
thay need to be seperate as ofn has larger molicules than 410a so takes longer to leak

thanks again