View Full Version : Re charge procedure is it correct?



camel007
01-04-2013, 09:05 PM
Hi
Just put a Mitsubishi SRK50ZIX-S and had no gas in it( 2nd hand) and now it turns on but the inside fan is running but the shutters are closed and outside compressor not running?
Can u check my method please as below.

Evac for two hours down to 250microns
Fit gas and purge at gauges to get rid of air and invert
Both valves still open(should i have closed one?)
Unit not running at this stage
Fill with 1.4kg of gas but only took 1.1kg
let settle for a few minutes
Turn on to cooling and run
turn off( think i should have left it running?)
let 300g gas in
Disconnect gauges
Unit wont run

Have i done this correctly, have i #@$%^ it?

Hope you can shed some light on it or a least verify my procedure?
Cheers

install monkey
01-04-2013, 09:11 PM
3 minute delay on start up of outdoor unit, did u put the indoor cover on properly - u can prise the louvres into an open position - mitsi dont have a limit switch on the louvres- u can unplug the louvre on the indoor pcb.

install monkey
01-04-2013, 09:13 PM
http://www.mediafire.com/view/?enugolbss5lfge4
similar uk version - service manual

camel007
01-04-2013, 09:14 PM
The problem is not just that the louvres dont open its more that the thing dont start up ie the outdoor fan is not turning?

install monkey
01-04-2013, 09:17 PM
outdoor fan will start up about 20 seconds before the compressor starts- check ur connections on the interconnecting.

camel007
01-04-2013, 09:20 PM
OK will do and thanks for the link but does my charging procedure look sound to you?
I have another one to fully re charge and was wondering if i had caused damage somehow by the way i charged it?

install monkey
01-04-2013, 09:26 PM
page 32 of the manual shows a flow chart, best to give it a long vac if the service valves were left open.
your method is ok except for prior to vaccing - pressure test with oxygen free nitrogen to upto 40 bar- if r410a to proove all is ok before vaccing

camel007
02-04-2013, 04:03 AM
Hi
FYI the problem was i did not have the original remote i bought a universal remote that appeared to work (made all the beeps etc) but in fact didnt. Found a remote and away it went!
Thanks for your suggestions

kefah
02-04-2013, 06:35 PM
pressure test with oxygen free nitrogen to upto 40 bar- if r410a to proove all is ok before vaccing

are you sure that he must pressure test to 40 bar or 4 bar

stufus
02-04-2013, 10:44 PM
are you sure that he must pressure test to 40 bar or 4 bar
Fookin 4bar !!!!!!! are you kidding me??
40-43 bar depending on manufacturers specs
Cheers
Stu

bigspee
22-04-2013, 05:52 PM
Was just about to say you sure you have the correct remote! Honest! Lol