26-02-2013, 08:21 PM
Hi guys sorry to bother but I am really desperate what to do with one Carrier water chiller 30 XA Carlyle screw compressor . . . :o


Low oil pressure indicate on controller the old one not that new ( slow ) .

Found on oil pressure transducer trace of oil and lose transducer and was leaking but very very slow .

I changed transducer but after while again the same fault .

What should to do next and make sure is just missing oil from compressor ...


Thanks for any advice .

Have nice Evening


P.S Can I just top it up or replace all oil ... ???

Grizzly
26-02-2013, 08:39 PM
Hi.
Have you considered the fact that the oil filter may need replaceing?
Grizzly

james10
26-02-2013, 10:36 PM
Hi.
Have you considered the fact that the oil filter may need replaceing?
Grizzly
Far too easy that, in fact the oil filter is the easiest filter in the world to change

Palkoper
27-02-2013, 07:43 AM
How to confirm is definitely just OIL Filter ... ? D

Palkoper
28-02-2013, 05:17 PM
sort it thanks

2007eng
05-06-2013, 06:12 AM
Check the difference between the discharge pressure & oil pressure, should not exceed 50 psi.

goshen
05-06-2013, 01:10 PM
Hi
how long after start up do you get this fault?
check on the prodialog screen oil level input , this will give you some indication what your problem is .