26-02-2013, 08:03 PM
Hi All,
We have been having some issues with RZQS125C7V1B condensers coils leaking on the passes. We have had three become faulty now. All have been changed under warranty. Daikin decided to look into this and sent out an engineer to investigate. I have attached his findings which I find very strange, they look to me like a cover up for the defect in there coil designs.
Daikin report
We attended site to investigate and check why the condenser coil has failed within 6 Months.
We arrived on site and checked the indoor unit. The indoor unit’s application is to maintain a comms room temperature of 19c and prevent the equipment from overheating. The room is small, measuring 4.5m by 3m. There is little IT equipment installed as shown in the photos below.
We monitored the temperature and the room was at set point. The unit would start and drop the coil temperature down to zero degrees Celsius for about 3 minutes then shut down. The unit would then stay off for a further 3 minutes and restart, and constantly repeats the same cycle.
The issue of the coil failing is due to the insufficient heat load in the room, causing the unit to short cycle. The constant short expansion and contraction of the coil outside in such a short space of time has led to the failure.
The outdoor and indoor capacity is too great for the load of the room and the potential for failure will remain unless addressed. We recommend reducing the size of unit as it is too large for the room and its heat load. If this is not addressed, then no warranty will be given to this system as future failures will occur due to the miss application of the system.
My questions are:
Has anyone heard of this before?
How long would you think a system should run for to make sure it does not cause damage?
Daikins case above therefor means every coil I have changed in the last couple of years is due to the system being oversized?
I know the system is about 1.5kw over sized due to the area being a server room and we want to allow for increased heat loadings.
Any advice would be great as our customer also had a copy of this report and is asking tough questions.
Cheers
We have been having some issues with RZQS125C7V1B condensers coils leaking on the passes. We have had three become faulty now. All have been changed under warranty. Daikin decided to look into this and sent out an engineer to investigate. I have attached his findings which I find very strange, they look to me like a cover up for the defect in there coil designs.
Daikin report
We attended site to investigate and check why the condenser coil has failed within 6 Months.
We arrived on site and checked the indoor unit. The indoor unit’s application is to maintain a comms room temperature of 19c and prevent the equipment from overheating. The room is small, measuring 4.5m by 3m. There is little IT equipment installed as shown in the photos below.
We monitored the temperature and the room was at set point. The unit would start and drop the coil temperature down to zero degrees Celsius for about 3 minutes then shut down. The unit would then stay off for a further 3 minutes and restart, and constantly repeats the same cycle.
The issue of the coil failing is due to the insufficient heat load in the room, causing the unit to short cycle. The constant short expansion and contraction of the coil outside in such a short space of time has led to the failure.
The outdoor and indoor capacity is too great for the load of the room and the potential for failure will remain unless addressed. We recommend reducing the size of unit as it is too large for the room and its heat load. If this is not addressed, then no warranty will be given to this system as future failures will occur due to the miss application of the system.
My questions are:
Has anyone heard of this before?
How long would you think a system should run for to make sure it does not cause damage?
Daikins case above therefor means every coil I have changed in the last couple of years is due to the system being oversized?
I know the system is about 1.5kw over sized due to the area being a server room and we want to allow for increased heat loadings.
Any advice would be great as our customer also had a copy of this report and is asking tough questions.