26-02-2013, 09:19 AM
The patient - Daikin RYP 100 L7W1

Issue - needs a capacity setting adapter to commission the new board?????

Never come across this before :confused:

Anyone care to enlighten me as to the why and where of this "adapter"

Thanks chaps

frank
26-02-2013, 09:55 AM
When the unit leaves the factory, it has the 'Capacity' setting installed in the EEPROM via software, as the outdoor boards fit multiple size units.

If you replace the outdoor board, or indeed the indoor pcb, you need the capacity setting resister to tell it what capacity it is supposed to work at, i.e. 7.1kW, 10kW, 12kW, 14kW

It is a small resistor that just plugs onto the pcb.

Whoever sold you the pcb should have advised that the resistor was required

TRASH101
26-02-2013, 10:14 AM
Thanks Frank :)

Couldn't buy through a more direct source as company policy don't like me sourcing through non account stockists.

Well they'll just have to keep using the "leccy" heaters until it gets here LOL

Cheers again

VRVIII
26-02-2013, 05:19 PM
Trash,

You should have receiced instruction with the PCB, there are 3 x jumpers on the new board that may also need to be cut and 2 x connectors that must be removed form original PCB and refitted to the replacement.

Jumpers:
JH = Compressor type
J4 = Voltage selection
J5 = Cooling only / heat pump

TRASH101
27-02-2013, 01:28 PM
Yup got them

TRASH101
27-02-2013, 01:30 PM
Although in the case of JH what is so different about Daikins own comp so as to require that jumper..........you any ideas on that VRVIII

Thanks

Trash

Darrenp
27-02-2013, 01:57 PM
You can prob use the old one from board taken out , then set dip switches to relevant settings , if in doubt ring daikin tech @01932 879 000 uk