View Full Version : Foster query
eam1956
23-01-2006, 04:58 PM
Just looked at a Foster freezer cab model LR400ADU apparently taking a trip switch out every few hours. Guessed it could be a defrost heater u.s. but there is no manual defrost initiator on the control (Foster CDC1L). I held in the bottom two buttons on control and sure enough the trip went out after a few seconds. Is this how you initiate a defrost on this model? Had no time to investigate more- returning in the morning, any help appreciated.
eam1956
23-01-2006, 07:45 PM
No, its taking the trip out on the supply board which supplies all the sockets in the kitchen.
chillin out
23-01-2006, 08:23 PM
I agree with Mr Magic, The first thing I would do it disconnect the heater wires and test with a meter.
Chillin:) :)
rbartlett
23-01-2006, 09:32 PM
if you push the
1/2 snowflake +1/2 water drop button
plus the
hand/ v button
that should initiate a defrost
cheers
richard
eam1956
23-01-2006, 10:37 PM
Thanks for that.