View Full Version : valves are open why is the airconditioner pumping down.
dmonte
22-01-2013, 09:16 AM
When the Valves are open, why is the airconditioner pumping down. Unit contains full charge 4.5 kgs of refrigerant. Where can the blockage be??
airconair
22-01-2013, 11:02 AM
hey dmonte you'll probably find your lev coil is rooted or come loose from the valve... most coils from manufacturers go for around 30-50 bucks in oz
passandscore
22-01-2013, 05:29 PM
Check the filter/drier. Is the expansion device a capillary tube? If so rule it out.
The Viking
22-01-2013, 08:30 PM
New install?
Any brazings?
OFN used?
Proper vacuum?
Manufacturer?
Model?
Existing unit?
Any works done on it?
All these questions....
:cool:
.
snave107
22-01-2013, 11:57 PM
You have your gauges hooked up? Also check the filter drier temp. Inlet/outlet for a TD. may be right there.
How do the compressor valves sound. loud? Sound like they are under load? Sounds to me with the problem given is a restriction in your high side.