Should a reciever be used on a capiliary exp device system, I am replacing a small condenser set it comes with one fitted I suppose I could cut it off but can it be left on

Cheers

install monkey
19-01-2013, 03:38 PM
no, when selecting condensing units,you select duty and expansion device either capillary or txv

monkey spanners
19-01-2013, 05:19 PM
Should not use reciever in cap tube system, it will fill the evaporator in the off cycle and then flood the compressor on re starting.

flyinkiwi
19-01-2013, 08:37 PM
Should not use reciever in cap tube system, it will fill the evaporator in the off cycle and then flood the compressor on re starting.

Agree - but I have seen a freezer fitted with a solenoid as a liquid stop valve, wired in paralell with the comp to prevent exactly that problem.

It was an Angelo Po if I'm not mistaken.

The MG Pony
18-03-2013, 06:45 PM
you gain nothing from it and it increases the refrigeration charge at no gain as well. I would personally remove it. The filter dryer serves as your mini receiver to ensure a liquid seal at the cap tube.

A cap tube system is a critical charge system for a reason.