View Full Version : Superheat!!!
Unreal688
05-12-2012, 05:38 PM
right then.... can some one just confirm for me what superheat we have. with the figures
R404a
Suction gas temp -15ºC
Suction pipe temp 2.5ºC
whats the superheat?
someone at work has made me doubt myself!! lol
Thankyou
Rob White
05-12-2012, 05:55 PM
right then.... can some one just confirm for me what superheat we have. with the figures
R404a
Suction gas temp -15ºC
Suction pipe temp 2.5ºC
whats the superheat?
someone at work has made me doubt myself!! lol
Thankyou
Superheat is the measurable (sensible) heat that is added to the saturated liquid - vapour mix.
Saturated liquid in the evap, in your case is evaporating (saturating) at -15 degc. You measured
the actual suction pipe to be about +2.5 degc.
The difference between -15 and +2.5 is 17.5 so your superheat is 17.5..............
But you knew that didn't you :) . Don't doubt yourself.......
Regards
Rob
.
Unreal688
05-12-2012, 05:56 PM
I dont know why i am doubting myself because i know it is 17.5ºC....
Unreal688
05-12-2012, 05:57 PM
HAHA.. yes I don't know why i did!!!!
Rob White
05-12-2012, 05:59 PM
..
:D
Good man :)
Rob
.