View Full Version : lennox rooftop unit
redroge
27-10-2012, 05:26 PM
I,ve got a lennox rooftop heatpump unit with a kp17 comfort controller ,the controller is showing Pb com fault (communication error),the interconnecting wirings ok as i,ve connected the controller directly to the outdoor unit which leaves either the kp17 controller,kp18 interface or the kp01 master module at fault, has anyone come across this problem before if so what was the answer.
cheers
Redroge
install monkey
27-10-2012, 05:54 PM
which pizza hut you on? haha . its a common fault- check your connections , if ok then its a new pcb
install monkey
27-10-2012, 06:12 PM
check the fuses on kp01 and your kp17 is plugged into terminal j22 http://www.mediafire.com/view/?fpz6dcwcizlepzc
redroge
28-10-2012, 03:38 PM
I,ve got 5vdc to the kp18 and 11vdc to the kp17 and yes its plugged into j22 ,main pcb or kp18?