I have a TL5g Danfoss compressor in a small clear door bar fridge that the motor cuts in and out every 20 seconds
I have replaced the start relay as contact were burned from it restarting lots of times with last owner
Have check gas and should be fine to run
I have bypass the thermo switch to eliminate that
But the run and start windings are low in ohm's
the should read 14.8 for both start and run
but they measure 9.9 run and 9.3 start
plus when i did have the old points cleaned up on the old start relay
the run coil gets very hot
could the internal windings become damage from stop and starting 100's of times with
old owner ?
thanks for your help