I have this problem : Daikin chiller model E oR F i am not shure so EWAD600AJYNH with a MCQuay compressor model HSA 32210Y11YV and is giving me this alarm AL215 high oil pressure difference : My first problem is that i have no documentation on this chiller because the end user lost it so i am in bad situation. After i week i should go to see the chiller but i must see before the manuals .Can anybody help me with the manuals ? My best regards .

Grizzly
18-07-2012, 09:23 AM
Hi Texanul.
I cannot offer a manual, however I am sure your problem refers to the oil pressure difference across the oil filter.
Therefore a oil filter change would be advised possibly a oil change would also be advised.
Grizzly

GHAZ
18-07-2012, 09:56 PM
hi friend as grizzy suggest check oil filters ,if its got a seperate oil seperator, then you need to check the filter from oil sep to back of compressor ,its housed in a 48cc drier housing,and check the solnoid valve +coil, and the filter inside the compressor is on the side just before large square inspection plate,it a round plate with about 8 bolts.If its the compressor with oil seperator attached to it then the oil filter is on right hand side of the oil sep looking from the oil sight glasses ,and you need m8 hex key and its has about 8 bolts screw in to a round plate

install monkey
18-07-2012, 11:39 PM
http://www.mcquayservice.com/McQuay/common/pages/literaturelistnew?prodtype=McQuay%20Factory%20Service&subprodtype=&maintopic=Service&topic=McQuay%20Factory%20Service&subtopic=

bratosin
21-07-2012, 06:59 PM
Hi. soud check oil level. probabli also the oil filter is durty. oil filter is in compresor not separattly. For any troble call me 0722500082 . if you give me serial of the chiler i give you documtation .

texanul
22-07-2012, 10:45 PM
The oil level is ok. The chiller is : DAIKIN EUROPE NV MODEL EWAD 600AJYNH-H R134 YEAR 2008 . So are you from Romania Bratosin ? I don`y have a serial number but i don`t think whould matters the serial !

install monkey
22-07-2012, 10:50 PM
http://www.mediafire.com/view/?329yjtgk49vrbpy
a lil literature may help

texanul
22-07-2012, 11:08 PM
I have this from daikin . I was really surprised because daikin belgia sent me this file but i dont have a documentation for the controller and a list of alarms . Thanks for your help monkey .

install monkey
22-07-2012, 11:13 PM
is it a pco controller

install monkey
22-07-2012, 11:25 PM
http://www.mediafire.com/view/?umbllqbk27ct170
service manual
http://www.mediafire.com/view/?bc02c6529e77b6b
pco controller
bet daikin didnt send you these!! :D

texanul
23-07-2012, 07:31 AM
LOL Nice . Those are like gold . Great files .Thanks a lot my friend .I am on the job now. :)

texanul
05-08-2012, 11:44 PM
Man finally i was to see that chiller . The problem i have now is that the controller is another kind of pco never seen before . The pco have six buttons : Instead of alarm is a left arraow instead of menu is a right arrow , insted of on/off button is a page . That was the upper part of buttons . Lower part is normally up arrow down arrow and enter . Second problem when i am traing to change some parametres i need to introduce a pass ,double pass of 5 digits . All the pass i know from daikin is 1234 and 1914 .I never saw this kind of double pass of 5 digits. I must remind you my chiller is a EWAD600AJYNH-H with a MCQuay compressor model HSA 32210Y11YV . All the papers i have is EWAD600AJYNN-H MODEL.Please help my my friend if you can .