View Full Version : mitsi city multi pefyp32vmse



install monkey
28-05-2012, 09:32 PM
indoor unit on simplified room controller-pac se51 cra
start up and controller illuminates then after 30 sec dissappears
there is the round dot to indicate power
indoor unit does nothing

indoor 240v input , live to neutral and live to earth neutral-earth 0v
indoor address 111 remote controller address 11
test condensate float swich - open circuit-ok= no water in drip tray
no fault indicated on the g50
there is a vin card on the room for lights but i dont think he ac is controlled off this
20mm glass fuse ok, rh led lit lh led not lit- tried jumper pin swe to try test fan/drainpump- nothing
anything else i could check or plan b swap the board with a spare unit

stufus
28-05-2012, 09:46 PM
Is that a 12v or 30v controller??
Indoor unit can't have an address above 50 , controllers are automatically denoted in 100's ,so a controller set to 11 is actually 111 .
Cheers
Stu

install monkey
28-05-2012, 09:48 PM
29v dc connected on the m net

Is that a 12v or 30v controller??
Cheers
Stu

stufus
28-05-2012, 09:51 PM
Swap the controller first.
Cheers
Stu

29v dc connected on the m net

stufus
28-05-2012, 09:53 PM
Is the controller listed on the G-50

install monkey
28-05-2012, 09:56 PM
yep- but starting it on the g50 has the same problem- i know if an indoor has no 240v then the controller will indicate all ok then dissappears - but 240v ok,glass fuse ok and as usual the pcb is 6 inches from the stud wall with the drain pipe in me way

stufus
28-05-2012, 10:18 PM
Conversation has been relocated to the darkside:cool:

JoeAT50A
29-05-2012, 07:56 AM
Outdoor SW2-1 ON for centralizing, SW2-2 ON to virgin start (new grouping via G-50A)

regcooldude
29-05-2012, 06:06 PM
Make sure there is no 3 wire adaptor wired to a window switch

install monkey
29-05-2012, 07:43 PM
returned today- checked controller was registered as 111 ok
swapped pcb with a 63 unit, adjusted the dip switches for a 32 unit- and all working- thanks for the tips but finally sorted- (i was the 2nd person to attend as the 1st lad said it was knackered and parts missing!!!- i only found the cover for the pcbs off- i think he only had small ladders and couldnt be arsed)

stufus
29-05-2012, 08:38 PM
Good monkey:p
Cheers
Stu