27-04-2012, 10:03 AM
hello friend, i have problem with mitsubishi kx2 error code E34, how can i solve it

install monkey
27-04-2012, 07:35 PM
• Abnormally low current (or no current) detected by [CT] on L3.
• Open phase detected at L3 (secondary side of contactor).
E34
-
Compressor current
• Abnormally low current (or no current) detected by [CT] on L3.
• Open phase detected at L3 (secondary side of contactor).
• Error on inverter board.

MR T
30-04-2012, 04:41 AM
thanks ok now i need to replaced the inverter board

iskan
04-05-2012, 06:14 AM
hi... good day to all.

i have 1 problem with kx2 system.. 1st error code e4. then i repair signal cable. i dont know how to reset system. then i power off system indoor and outdoor unit. after 20 minit, i power on system but error code e2 and e3 display at indoor remote control. any how to resolve this problem. indoor only 4 unit. outdoor single module only.