Hi
Does anyone know of a link for starting methods for 3 phase semi hermetic compressors.
Thankyou.
Bernard
Rfcont
21-11-2005, 08:54 PM
Hi Bernard!
Starting method (Not important what type compressor)depends very much from power of the motor
It is very nice idea do it with the softstarter.
chillin out
21-11-2005, 09:00 PM
Hi bernard,
Is this what you mean?
http://www.johnson-pump.com/Horticulture/default.htm?page=/Horticulture/quickstart-motor.htm
OR
http://www.cacciaelettronica.it/products2_2117.htm
Chillin:) :)
chemi-cool
21-11-2005, 09:19 PM
Hi bernard,
A soft start is a good one.
YY is another one.
And direct start.
These are the most common ways to start a semi hermetic compressor.
Chemi:)
wambat
21-11-2005, 11:44 PM
Hi
Does anyone know of a link for starting methods for 3 phase semi hermetic compressors.
Thankyou.
Bernard
You may find this informative
http://www.lmphotonics.com/m_start.htm
bernard
24-11-2005, 08:15 PM
Thankyou
The links gave me all the info I needed,sorry for the delay in my response but I,m just so busy with work at the mo.
Kind Regards
Bernard
Peter_1
25-11-2005, 08:16 PM
http://www.ecopeland.com/Literature/eCopeland/en_Art_Part_Winding_Motors_SH.pdf
bernard
26-11-2005, 09:05 AM
Thanks Peter
Most of the part wound motors I have seen have their timers set for 1 second.Is this a standard setting or should it vary depending on size ?????:confused:
Thankyou
Bernard
Peter_1
26-11-2005, 10:12 AM
We set it also that short: 1 sec.
In Y-D start you have to set the time as long the current in Y isn't 'flattened' . You can only set this by measuring the start AMP's and time when the current drops and stabilises. This will be the time for the Y-run.