View Full Version : Carrier A100 code overload - ground fault on 1800 vector any ideas plz



deanCool
01-04-2012, 04:48 PM
Unit shut down on code 30 secs after restart

moggy66
01-04-2012, 08:15 PM
Try changing the ground fault module...

Edvin
02-04-2012, 03:16 PM
Unit heating or cooling? Whatch wich contactor engages when the unit goes off - that cuircit has the melfunction. More common that one of the heating tens goes short to ground.

sonkax
04-04-2012, 05:06 PM
well first tell us please, if unit is with OGF or overload relay

flyinkiwi
25-04-2012, 04:48 AM
Try changing the ground fault module...

Yeah, what Moggy said.

Fitted second replacement OGF (on same unit) to a Vector late last year.

chrisGreece
04-09-2012, 06:32 PM
i have the same problem with a Vector, i searched all the electrical circuits that OGF module controls and i didn't found any leakage.Also checked the overload factor at the start up and it was also inside the limits, but the unit shuts down after 3-4 minutes of operation.Any ideas exept replace the OGF mudule?