View Full Version : HEPA Filter for low temp (-15C)



blackheart_hui
27-03-2012, 06:22 PM
Hi guys, I new to this group & glad to join the group to discuss Refrigeration.I need some help for conditioning of the air. If anyone have come across the following problems, please advise.Previously, I have a fresh air system for food process. Air is conditioned through 3 AHUs to +2C & is filtered by HEPA from AAF of AAF AstoCel 1. Recently I done a upgrade of the system & brought the air temp down to -15C. However I noticed that HEPA freezed after 30 min of operation & system pressure went from 1.6KPa to 4KPa. When we revert back to the old parameters, system pressure went back to 1.6KPa.Therefore I am asking if anyone have done a project like this & have come across this problem. Also, do anyone know if there are HEPA filtration for temp as low as -10/-15C?Thanks in advance, Hui

aramis
27-03-2012, 07:51 PM
Never had this problem in particular, though I know you have to change the type of filter if you have now high relative humidity or the velocity profile changed.

You should contact the filter supplier.

blackheart_hui
28-03-2012, 03:08 AM
We are currently seeking advice from AAF on the suitable type of HEPA.
The air velocity was changed from 143 to 165m3/min

mad fridgie
28-03-2012, 04:31 AM
Your filter is not freezing up, it just becoming blocked with ice particles that are suspended in the air.
Think of it as "Ice dust"

blackheart_hui
28-03-2012, 11:05 AM
Hi mad fridgie,

That certainly ring a bell!!! I noticed the area after my -15C coil & before the HEPA to be fill with 'snow'. You know of any product on how we can 'catch' these dust out from the air before reaching the HEPA?

Thanks, Hui

aramis
28-03-2012, 02:13 PM
It looks like you are working in an oversaturated region, thus the fog.

Drying the air may help.

install monkey
28-03-2012, 10:14 PM
if its a fresh air system the surely you fiter the air then cool it-thus eliminating your hepa filters frosting up

Hi guys, I new to this group & glad to join the group to discuss Refrigeration.I need some help for conditioning of the air. If anyone have come across the following problems, please advise.Previously, I have a fresh air system for food process. Air is conditioned through 3 AHUs to +2C & is filtered by HEPA from AAF of AAF AstoCel 1. Recently I done a upgrade of the system & brought the air temp down to -15C. However I noticed that HEPA freezed after 30 min of operation & system pressure went from 1.6KPa to 4KPa. When we revert back to the old parameters, system pressure went back to 1.6KPa.Therefore I am asking if anyone have done a project like this & have come across this problem. Also, do anyone know if there are HEPA filtration for temp as low as -10/-15C?Thanks in advance, Hui

blackheart_hui
02-04-2012, 09:46 AM
hi guys, thanks for all your help.
I shifted the HEPA upstream before my -15AHU. Also explained the mystery for the chocked filter. Thanks You