View Full Version : DAIKIN FXFQ80P9 information about water condensation
boski
09-03-2012, 01:26 PM
hi everybody ;
I need information about water condensation for daikin FXFQ80P9 indoor unit. There ll be about 1500m3/h air at 35C and with %80 humadity and it ll be cooled for 10C and %50 humadity . My question is how many kg water ll be condensated in 1 hour? Sorry for my English but I ll be glad if someone explain and find me a solution.
Thanks
boski
12-03-2012, 12:24 PM
any idea ?
frank
12-03-2012, 03:23 PM
To calculate kg/hr moisture removal
kg/hr = vol x delta kg/kg x 3600 / specific volume
You need to use a Psychrometric Chart
from your figures - 35C @ 80% and 10C @ 50% the results are
Vol = 0.416m3/s
Delta kg/kg = 0.0256
Sp Vol = (0.806 + 0.914/2) = 0.86
so
kg/hr = 0.416 x 0.0256 x 3600 / 0.86 = 44.57
Looking at the spec sheet for the FXFQ80P9 it will not handle the volume or the humidity
The maximum volume on high speed is 1410m3/hr but more importantly, it is only rated at 9.9kW cooling duty and you need 15kW
nike123
13-03-2012, 03:13 AM
What you asking is this:
http://i42.tinypic.com/v3hhc9.png
That is if you have dehumidifier which will dehumidify all new air in one pasage. But, that is not your case.
You have air-conditioner which will cool same air and dehumidify it in multiple pases through it.
This is from tehnical data:
http://i40.tinypic.com/anmypk.png
At begining you will have this:
http://i40.tinypic.com/2igp106.png
At end you wil have something like this:
http://i39.tinypic.com/av4mlz.png
boski
13-03-2012, 03:36 PM
thanks for help. i ll look for thoose softwares if they can help me