It is common practice to add a small amount of propane to the low stage in a cascade system. I know that someone, ASHRAE maybe, had defined a minimum ratio of propane to refrigerant for flammability reasons, does anyone know what that is or where I can find it in writing?

chemi-cool
09-02-2012, 07:34 PM
I add 1% > 2% to 404 507 systems. it does wonders with oil return.

Try google, if its on the web, you can find the info.

Shaukat
18-02-2012, 12:40 PM
HI,
What is role of R-290 in oil returning?

chemi-cool
18-02-2012, 05:25 PM
R-290 is a very good oil carrier.

padraic
18-02-2012, 06:17 PM
we use r290 in in -80C ultra low freezers... the r290 is mainly for oil return purposes 10grams is all we use in each cabinet

michaelm
19-02-2012, 02:13 AM
we use r290 in in -80C ultra low freezers... the r290 is mainly for oil return purposes 10grams is all we use in each cabinet

B”H

Padraic,
10 grams of R-290, what it is a percentage of the totals charge.

Shaukat
19-02-2012, 03:16 PM
fine, i am going to make ultra deep freeezer in next month, i will do it, thanx

Luke.G
19-02-2012, 04:05 PM
yeah, worked on one -80 and we had to charge the low side with pentane which is a flammable liquid, but again the only reason was for oil return and the plate give us a weight in oz to charge how much of it in the low side