Hi everybody
Have anyone operated reverse cycle water-to-water chiller/ heatpump ?? any need any special in operation for them ?
Thanks

AlexG
08-02-2012, 06:04 PM
some manufacturers are specialized in this type of chiller. I mean u have to change only water direction, no 4-way valve on ref pipes. But controller must manage outlet chilled water temperature to avoid freezing in both modes, heating and cooling. That's important.

reff
09-02-2012, 11:31 PM
3-way, 4-way

NoNickName
10-02-2012, 08:19 AM
Yes, many of them. In Norway and Sweden it's quite common. No specific care is needed. Control is on condenser, and evaporator is only controlled for freezing protection.

wta12
10-02-2012, 04:11 PM
Thanks a lot for the answers. My schematic exactly like the reff three way attachment.
@ AlexG : could you name some manufacturers are specialized in this type of chiller ? I want to check different technical specification.
@All : Have you any documents/recommendation related control multi-chiller plant of this kind chiller especially in control sequence and change-over heating/cooling control ?

r.bartlett
10-02-2012, 05:08 PM
I assume it should be a sealed system due to potential legionella?

AlexG
10-02-2012, 05:55 PM
WTA, check websites of Climaveneta or CIAT. I suppose that Carrier or York make this type of units. What is your e-mail?

wta12
11-02-2012, 02:01 PM
I assume it should be a sealed system due to potential legionella?

we use closed-loop with chiller and dry cooler. Many manufacture have this kind of system but cause rarely use in our location ( we are the first) the information about control, operation is uncleared with us.

wta12
11-02-2012, 02:39 PM
I assume it should be a sealed system due to potential legionella?

we use closed-loop with chiller and dry cooler. Many manufacture have this kind of system but cause rarely use in our location ( we are the first) the information about control, operation is uncleared with us.
@alexG : Please check the PM

AlexG
11-02-2012, 06:51 PM
wta, why dont u use air-to-water heat pumpes? High humidity?

wta12
20-02-2012, 03:11 PM
Becausa architect and acoustic restriction. dry cooler and water-cooled chiller is only variant