View Full Version : fujitsu inverter doesn't start when the outdoor temp is below zero
Greek_engineer
16-01-2012, 11:02 AM
hello my friends!
Does anyone know why a fujitsu inverter ,24000 btu -R 410 ,doesn't start operating when the ambient temperature is below 0 Kelsium?
During the day when the temperature rises it operates normaly as usual in heating mode.
Thanks a lot!
install monkey
16-01-2012, 08:49 PM
Faulty outdoor sensor?
Greek_engineer
16-01-2012, 08:59 PM
maybe, but it generates me many questions why this is always happening at the dawn when temperature is below zero.I suppose that the control cuts the system as a protection from icy conditions.
However, this is not correct since the system is inverter (designed to operate at low temperatures) and next to fujitsu is installed a daikin inverter split(in another room) that operates without any problem at all.
james10
16-01-2012, 09:08 PM
The moral is Daikin is better than Fujitsu
install monkey
16-01-2012, 09:36 PM
any flashing lights on the indoor unit? try holding the outdoor sensor when its not running to see if it starts
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.