PDA

View Full Version : Compressor Label R134a but the label inside the unit is R404a



Mhikhel
28-12-2011, 05:30 PM
I will repair a Desmon chiller I see the label inside the unit it is R404a refrigerant but when I see the compressor the label is R134a. That why I cannot start to repair because I dont know what refrigerant I will use. Can you help me with this. Thank You

install monkey
28-12-2011, 05:37 PM
has the compressor been changed before? what does the expansion valve say- probably best to contact the manufacturer for comfirmation

Name: FRAU FOODSERVICE, S.A.U. (http://www.desmon.it/index.php?option=com_contact&task=view&contact_id=8&Itemid=7)
Telephone: (+34) 902 20 10 69
Fax: (+34) 93 348 15 09

chemi-cool
28-12-2011, 06:35 PM
In your ambient, it would most likely to be R-134a, Difference between compressor for 134 and 404 is displacement.
Check the running pressure, it might help you.

coldcraft
30-12-2011, 02:07 PM
Check the system pressure after it has been standing off for some time,check your ambient temperature then use a comparator to get the pressure/temperature readings and you will then know what the system is charged with

savoc
15-01-2012, 09:49 AM
check your t.x valve.