View Full Version : dwm copeland compressor



redroge
04-11-2011, 06:36 PM
has anyone had problems with excessive vibrations on dwm compressors,it pumps ok and the heads are ok but there,s excessive vibration.
the compressor is on a delonghi chiller on a gantry on a roof with access via a vertical ladder.

stufus
04-11-2011, 09:52 PM
Had something similar on a Climaveneta,
Turned out to be the discharge pipe was stressed by the brackets .
Loosened the brackets and allowed the pipe to take it's natural position, re tightened job done
Cheers

Stu

Grizzly
04-11-2011, 10:17 PM
Good advice Stufus.
A situation that is more common than many realize.
Grizzly

redroge
14-11-2011, 06:05 PM
thanks for your replies but on this chiller there is a five foot flexible from after the muffler to the condenser

stufus
14-11-2011, 07:46 PM
OK
But what connects the discharge valve to the muffler ??Did you try loosen the brackets at the muffler??
Have all transport plates/bolts been removed??
I'm not saying you don't have another issue, but the slightest bit of stress tension promotes resonance which amplifies the problem.
Cheers
Stu

moideen
15-11-2011, 08:28 AM
it may happen due to seize of connecting rod to shaft journal or any discharge read may broken.(this my site experience).

moideen -dubai.

redroge
15-11-2011, 06:48 PM
there is one bracket holding the discharge pipe to the compressor after the muffler and before the flexible its been ok for about five years

stufus
15-11-2011, 08:12 PM
Should have asked this earlier ..
Is the vibration local to the comp or is it travelling throughout the chiller and through to the gantry.
Have you tried levering the suction and discharge pipes with a podger bar or a big shifter to pinpoint the source.
Cheers
Stu

Magoo
15-11-2011, 10:32 PM
Could have a leg hanging out of bed [ busted conrod ]

install monkey
15-11-2011, 10:37 PM
have u checked the steelwork on the gantry,maybe the anti vibration mounts have deteriorated?

redroge
16-11-2011, 06:50 PM
the vibration is due to the compressor as the other compressor on the chiller is ok ,as i said before the heads have been off and all looked ok

D.D.KORANNE
17-11-2011, 06:17 AM
if you operate the compressor free of its piping , suction and discharge on a test bed , it may not vibrate . but as you install on system , it vibrates ........... if the answer is yes ...... you will have a partly broken discharge valve reed .........just check