we have just inherited a building to maintain which has a 18mnth old air source heat pump which is condensating heavily and water runs out and down the pathway has anyone got any ideas why it should condensate so heavily please?

Andy

Tony
17-10-2011, 10:50 AM
Is it big enough for the room it is cooling/heating?

Gideon Beddows
17-10-2011, 10:55 AM
in heating mode the outdoor unit becomes the cooler and so will make condensation.

Its possible this is normal operation?

It 'may' be short of gas in which case you. In which case you'll need a full leak test / repair / re-charge - or, if you have the time - reclaim the refrigerant and test the weight against the commissioning / nameplate charge details.

Hope that helps?