Hi everybody!
I read now the thread about it. Unfortunately the replies weren't good ,there is a bigger problem.The oil can go only one way out from compressor,through the oil heat exchanger.The exchanger is broken between the oil and the refrigirant.you have to change the exchanger or the oil always will disappear,and finally it goes in to the evaporator and the unit won't be able to chill

chillerman2006
06-09-2011, 04:30 PM
Well stick your comment on the thread http://www.refrigeration-engineer.com/forums/showthread.php?32861-Carrier-19Xr-Oil-problem I could only work out what you meant as both threads are in top 5 at the minute....

Your new thread on it's own dont make much sense mate

R's chillerman

james10
06-09-2011, 09:16 PM
The oil is miscible either the refrigerant it will migrate with it if the oil heater is off and the water us left circulating through the water boxes