10-07-2011, 04:56 PM
I am having problems with with my compressor unloading for no apparent reason other than possibly a faulty bi-metal disc inside my Copeland scroll compressor (38ARQ) Here's the stats.
outside air temp 67 f
suction presser 55psi
high side 200
discharge air temp 57 f
amp draw 18.5, 20,18.5
refrig R-22
customer wants 68 f consent. (server room)
system has ecomonizer/compressorlockout
5 ton
I had this condenser unit installed last spring 4/10 and been running very well until recently 7/11 I noticed it wasn't putting out cold air. Upon inspection I noticed the condenser was running with compressor and fans on. My initial guess was a broken valve. At this time I did not know about ASTP. So apparently when the compressor's internal temp reaches 300 f the scroll elements unloads while running. I shut down the unit for 1 hr per instructions. I started it up and it ran good for about 24 hrs. My coils are clean and filters are replaced ,we don't have power flex problems. So I'm not sure what to do next. Perhaps I'm not understanding whats happening.
Anybody have any ideas?
Thanks for any help.
outside air temp 67 f
suction presser 55psi
high side 200
discharge air temp 57 f
amp draw 18.5, 20,18.5
refrig R-22
customer wants 68 f consent. (server room)
system has ecomonizer/compressorlockout
5 ton
I had this condenser unit installed last spring 4/10 and been running very well until recently 7/11 I noticed it wasn't putting out cold air. Upon inspection I noticed the condenser was running with compressor and fans on. My initial guess was a broken valve. At this time I did not know about ASTP. So apparently when the compressor's internal temp reaches 300 f the scroll elements unloads while running. I shut down the unit for 1 hr per instructions. I started it up and it ran good for about 24 hrs. My coils are clean and filters are replaced ,we don't have power flex problems. So I'm not sure what to do next. Perhaps I'm not understanding whats happening.
Anybody have any ideas?
Thanks for any help.