Hi All
Hope someone can help.
I have been called out to a VRF with a P22 fault. I ordered up and fitted today the upgraded IPUD board. I did not replace the fan as the winding are ok, aprox 3.1 ohm.
The P22 fault has cleared but the fan wont run and thus goes out on HP.

I have had the same faults on 2 other units over the last 12 months but I have changed the IPUD board and the fan at the same time and hey presto were away.

I suspect the board (the new one has failed) but can someone give me the head up just in case im missing something obvious.

I have been in touch with Toshiba Tech support UK and they say i should change the fan, and the board my be faulty. But the resistance of the fan is within there quoted tolerence.

Any help appreciated

superswill
29-06-2011, 10:18 PM
i might be wrong but from memory do you have to add additional heat paste to the IPD's?

Rob123
29-06-2011, 10:32 PM
Hi Paul
Yes mate, the upgraded IPDU comes with with a large tube of heatpaste. Which was generously applied..
I should have added that I did have equal voltage across the IPDU output of aprox 57volts fan connected and 82 volts when i ditched the fan.

daveyboy123
29-06-2011, 10:36 PM
Ive changed plenty of these, and always changed the fan motor regardless.
Yes there is a heat paste that should be fitted.

Toshiba obviously have a big prob with these.

billywizz
01-07-2011, 06:23 AM
Had similar problems and new type IPDU's which are much bigger fixed the problem. Also cleaned off all the old heatsink paste and repasted, I could usually tell which IPDU was faulty of several units by spinning the fan blade the faulty one seems to have a slight drag as if the bearing is gripping which disappears when leads are removed from the IPDU. Many similar posts about this problem before.

Rob123
01-07-2011, 09:49 PM
Billywizz...
I have noticed the same thing... the fan does drag... even on the brand new (larger) IPDU.
Im back there Monday morning with another new IPDU and a new fan. I will let you know how it goes.

Rob

Rob123
04-07-2011, 08:07 PM
Hi All