hey guy, i m confuse with this.... hopefully can get some explanation...

- system cooling capacity KW
- compressor capacity KW
- expansion valve kw?

for example if chiller capacity 100KW, what is the relation between compressor, condenser, expansion valve, and evaporator....

can share some formula & calculation for this?
thanks...
:confused:

Peter_1
23-04-2011, 10:54 AM
100 kW cooling, +/- 3 COP = 33 kW compressor capacity or 25 kW at a COP of 4
COP is a factor of the working conditions (LP versus HP)
Expansion valve is 100 kW at a certain evaporation capacity and a certain subcool and a DP over the valve

There are no formulas nor calculations for this, only manuals/selection tables of the different manufacturers.

ah fai
25-04-2011, 11:02 AM
thanks a lot... bro...
means we can see the system cooling KW from the expansion device... right!!!!

Peter_1
25-04-2011, 01:56 PM
Yes and no, you only can make a rough guess because the expansion system can regulate its capacity within a certain margin.

ah fai
04-05-2011, 06:05 AM