View Full Version : Fujitsu ductless heat pump/air conditioner doesn't work



jayryu
21-02-2011, 11:40 PM
I have a problem with Fujitsu ductless heat pump/air conditioner.
The Indicating light of "Operation" and "Timer" flickers.
The sequence is as follows.
1. Cut off the power to the unit.
2. Power on the unit
3. After about 3 ~ 4 min. " Operation" light flickers 5 times
4. "Operation" and "Timer" lights flickers 5 times simultaneously.
5. Flickering of both lights continues.

During this check, Indoor & outdoor unit doesn't work. Only air flow louver opens and closes.
Any recommendation?
If you gentlemen have service manual, I appeciate to share.
Fujitsu Model: Indoor ASU24RLXQ
Outdoor AOU24RLXQ

J.

stufus
22-02-2011, 07:53 PM
http://www.fujitsugeneral.com/PDF_06/OperationManual/(OM)ASU24-30RLXQ.pdf
Check that out bottom of page 16 small print
Sounds like the inverter board has failed ,count the flashes of the timer light ,it's probably 13 blinks
But i may be wrong
Cheers
Stu

jayryu
23-02-2011, 03:49 AM
Thanks stufus for your concern,
I 've got the service manual from Fujitsu america today. I am going to study it from now on.
If I find the cause I 'll post asap.
J.

stufus
23-02-2011, 08:36 PM
No problem let us know the outcome.
Cheers
Stu