View Full Version : Carrier 30rh090
HARRY 7
14-02-2011, 08:17 AM
I need to change the pcb of the B circuit of the unit.They tell me that the pcb needs
programming.Is this something that i can do it in the field?
james10
14-02-2011, 06:28 PM
request it preprogramed from the factory or you will need carrier to download the relevant programmes and software youd be better off getting carrier to install the board
HARRY 7
14-02-2011, 06:50 PM
Thanks james for reply.I was asking if i could avoid the preprommaning from carrier and do it myself.
james10
14-02-2011, 08:37 PM
No afraid not, you would need a carrier pc and software which is only available to Carrier
HARRY 7
15-02-2011, 03:24 PM
Thanks for the help james.
james10
15-02-2011, 08:46 PM
Where in the world are you Harry i might be able to put you intouch with the correct service branch
HARRY 7
16-02-2011, 06:14 PM
Athens..greece.
james10
16-02-2011, 09:22 PM
Here you go http://www.carrier.gr/