I'm new here and it's my first post. I'm from Brazil and need Help in a Carrier 23XL that i'm working on.
Actually machine is running but i have a alert message "High condenser pressure". I read some parameters that may help all:
Evaporator Refrig temp: 11,3c
Evaporator Pressure: 606,8 Kpa
Condenser Refrig Temp: 41,6c
Condenser Pressure: 1490,7Kpa
Discharge Temp: 56,8c
Oil Sump Temp: 56,8c
At Pic II i also have:
CHW in: 18,3c
CHW out: 15c
CDW in: 27c
CDW out: 34c
MTR AMP 80%
So if any one have ideas to help my chiller i would apprechiate a message.
Thanks in advanced!