Does anybody know what amp circuit breaker need's to be fitted for this unit? daiken FTXS90J wall hung split inverter
Thanks
lawrence1
23-01-2011, 10:15 AM
As the unit draws 4340watts (18amos) i would use a 25amp c/breaker with 4mm cable.
Lawrie
install monkey
23-01-2011, 03:46 PM
id go 20a d type-motor rated even though its inverter driven. the length of cable run will have an effect on the size of cable.